Visit MikeHolt.com
Indoor Pool Lightning Policy  

 
Image

We were recently contacted by a nurse researcher regarding lightning policies concerning indoor pools.

Here’s what she asked:
I am contacting you about a "lightning policy" at our Parks and Recreation indoor pool.  The National Electric Code Article 250 — Sections 250.1 through 250.4 require that indoor pools be grounded and safe from lightning strikes. According to management at the facility, which closes the indoor pool when pool staff hear thunder or see lightning outdoors, there is a risk of lightning strikes to indoor pool patrons.  As I am sure you are aware, there has never been a reported incident of a patron being killed by lightning in an indoor pool.

The closing of indoor pools during storms has recently been deemed an "urban legend" because there is no scientific evidence of the need for this policy.  The National Lightning Safety Institute, founded by Richard Kithil, recommends closing indoor pools based on the results of an Internet Google search of "indoor pool and lightning" (http://www.lightningsafety.com/nlsi_pls/indoor_pools.html).  The NLSI also lists several organizations who have position statements/policies that require indoor pools to close during storms.  These organizations either do NOT have these policies or their policies are based on the NLSI recommendation following the Google search. I have tried to contact the NLSI but none of the contact links are valid.

My query to you is to ascertain whether there is a legitimate risk to patrons at an indoor pool that has facilities up to code (NEC 250)
.   I have read several documents that support not closing indoor pools during storms. Thank you for your help.

The nurse researcher and her team are currently conducting a study to determine if patrons are being placed at risk by leaving indoor pool facilities during thunderstorms.

 

What do you think? We’d like to hear from you, so post your comment below. Dr. Hardin-Fanning, the nurse researcher can be contacted directly at fdbowe2@uky.edu.

 

Mike Holt’s comment: It’s a myth!
http://www.sportrisk.com/2011/08/the-myth-around-closing-indoor-pools-when-theres-lightning/
http://www.aquaticsintl.com/safety/when-lightning-strikes.aspx

 

 

 

Click Here to Post a Comment Click Here to View Comments Click Here to Unsubscribe
 
Image
 
Visit: Exam Preparation | Continuing Education | Code Products | Newsletters | and more
Copyright© Mike Holt Enterprises of Leesburg, Inc. All Rights Reserved This article is protected by United States copyright laws and may not be published without prior written permission.
Mike Holt Enterprises of Leesburg, Inc. 3604 Parkway Blvd. Suite 3 Leesburg, FL 34748
"... as for me and my house, we will serve the Lord" [Joshua 24:15]
Comments
  • What about a shower during storm, same as indoor pool or not?

    Joe  February 9 2016, 3:39 pm EST
    Reply to this comment
  • Reply from: Mike Holt   February 10 2016, 7:14 am EST
    Showers don't have a bonding grid...
    Reply to Mike Holt


  • Michael Koerner Oct 30 (6 days ago)

    to fdbowe2 Many may not weigh heavily on being struck by lightning in an indoor pool. But it does not mean it can not happen. There have been people struck by lightning in there house, this is a force of nature. A GPS may determine where you are located within a foot on the earth. There is nothing saying exactly where lightning will strike. If there was we would not need electrical power plants or solar power we would use lightning. Go conservative, in the land of lawsuits where "caution contents in this coffee cup may be hot" shutting down a pool for safety is the right thing to do. It is really nice to use common sense over scientific studies or myth's when it is the right thing to do.

    Michael Koerner  November 5 2015, 8:05 pm EST
    Reply to this comment
  • Reply from: Achuthan   November 5 2015, 9:29 pm EST
    As pointed out by Mr.Koermer, the main ingredients(brain inputs) for making professional are 1. Common sense 2. The professional knowledge. Both of these factors complement each other in a decision making exercise. Although indoor pools could be used safely, if adequate shielding GNDing etc are done theoretically, the commonsense factor comes into play since safety, higher risk taking etc., are involved in this case, as pointed out earlier. Hence, I feel that it is better to be out of the pool during lightning. Achuthan.N

    I
    Reply to Achuthan

    Reply from: Mike Holt   November 6 2015, 6:54 pm EST
    We can't run our world on what people think is common sense when we have data of over 100 years of experience (data).
    Reply to Mike Holt

    Reply from: Achuthan   November 6 2015, 8:12 pm EST
    "common sense" of a person is not what people think but inherited rather acquired out of many things. The commonsense level of an individual varies with age,exposure, and hence is different form person to person. It is a complex stuff. In fact we need commonsense to relies and recognize the common sense of the other person.
    Reply to Achuthan


  • Get out of the pool, remain in the building, wait for the storm to pass. Perhaps no one has been killed in an indoor pool in a hundred years....because they get out of the pool.

    Steve Fisher  November 3 2015, 8:56 pm EST
    Reply to this comment

  • I am old school, so my thought is better safe than sorry. Leave the pool, because nothing man made is 100% guarenteed.

    Tim  November 3 2015, 8:09 am EST
    Reply to this comment
  • Reply from: Mike Holt   November 4 2015, 6:58 am EST
    I work off of facts when I make a decision. Don't know any other way.
    Reply to Mike Holt


  • Competent persons need to complete a risk assessment!

    TVH  October 30 2015, 11:31 pm EDT
    Reply to this comment

  • I really don't know where Dr.Hardin-Fanning has gotten the idea that the NEC is the the governing entity that requires people to leave the pool area. However, as I get older and hopefully, more wiser, I, myself would get to somewhere I would feel was safer for myself than taking a risk. Experience has taught me to not trust anything in life 100%. Call me old fashion, but, I truly believe that there is a thin line between courage and stupidy, and knowing where that line is, is paramount in life.

    Bob L.  October 30 2015, 6:01 pm EDT
    Reply to this comment
  • Reply from: Achuthan   October 30 2015, 9:49 pm EDT
    Pl. note that Prof. Martin also feels, just I stated yesterday, that the indoor pool need not be closed provided all the Grounding precautions are taken. But he prefers closing it, so as I, since it could turn into life & death problem if some installation error is made. Life is more important that swimming and hence it is a wise action to close the indoor pool.

    Achuthan.N achuthan@presevi.in
    Reply to Achuthan

    Reply from: Mike Holt   October 31 2015, 8:50 am EDT
    Let's work on some facts: 1. Nobody in 100 years has ever been injured or killed in a pool because of lightning. Pools have a Faraday cage via the requirements of the NEC. There is NO reason to prevent people inside from enjoying the water in a pool...
    Reply to Mike Holt

    Reply from: Fran   October 31 2015, 10:39 am EDT
    Please be aware that I do not think the NEC is the governing entity that requires people to leave the pool area. My concern is people leaving the indoor pool area and exiting the building during thunderstorms (which we are finding a majority of people do). The 216 lightning deaths that have occurred over the past decade had one common attribute -- they all happened outdoors. The purpose of my research is to determine if indoor pool patrons are being placed at risk of a lightning strike by leaving a safe area (inside a building) due to policies that are based upon unsubstantiated fear. I contacted Mr. Holt for his expertise and I appreciate the comments from all of you who are experts in your field.
    Reply to Fran


  • The National Electrical Code (NEC) requires electrical systems in buildings, and especially pool shells and the metal around pools to be electrically bonded together. If the electrical wiring/grounding in the aquatic facility meets code, this indoor area is probably safer than within many buildings.

    The only danger from electricity, be it lighting or any other source, is voltage potential between objects which a person is near or in contact with. Any stray earth current from a lighting strike outside or to the building would cause all of the surfaces to rise and fall to the same level. This ?bird on a wire? phenomenon makes it safer than in the typical building. A possible exception would be if the pool shell were non-metallic, and therefore did not have the bonded rebar/metal shell of a common pool.

    Closing a pool cannot be a violation of the NEC, but it certainly should be an OSHA violation. To close an indoor pool during an electrical storms takes the patrons from an especially well protected indoor environment, and places them more at risk elsewhere - especially if they must go outside to leave !

    Scott Cline  October 30 2015, 2:57 pm EDT
    Reply to this comment
  • Reply from: Fran   October 31 2015, 10:40 am EDT
    We are finding the overwhelming majority of pool patrons exit the building when they are asked to leave the pool area.
    Reply to Fran


  • Mike,

    The quotes in the links by Dr. Vicki Weiss are totally wrong where this person states that it is a violation of NEC Art 250.4(A)(1)to close an indoor pool for lightning. The NEC is an installation code and has nothing at all to do with public or private policy regarding pool closings during lighting storms.

    Andy Kriegman  October 30 2015, 12:19 pm EDT
    Reply to this comment

  • I posed the question of whether an indoor pool should be closed when lightning is nearby to one of my former professors, Dr.Uman, who is one of the world?s leading authorities on lightning. Here is what he said:

    "That is a hard question to answer. In principle, one would not need to close the pool if all possible voltages on the metalwork, lights, etc. were properly bonded and grounded. The problem is , one cannot count on that, and since lightning will raise all voltages to a high level even with code grounding, there could still be voltage differences present to drive current through bodies. The danger in an indoor pool, I think, is drowning after a shock, rather than electrocution. I'd close the pool. Martin"

    Martin A Uman Distinguished Professor of Electrical and Computer Engineering 311 Larsen Hall University of Florida Gainesville, FL 32611

    Vincent Sancho, PE  October 30 2015, 10:33 am EDT
    Reply to this comment
  • Reply from: Mike Holt   October 31 2015, 8:51 am EDT
    Let's work on some facts: Nobody in 100 years has ever been injured or killed in a pool because of lightning. Pools have a Faraday cage via the requirements of the NEC. There is NO reason to prevent people inside from enjoying the water in a pool...
    Reply to Mike Holt


  • Frivolous Lawsuit fear.

    Troy  October 30 2015, 10:27 am EDT
    Reply to this comment

  • In my opinion, there are too many variables to make an all-inclusive and universal rule for indoor swimming facilities and lightning. It's very difficult to explain or prove a negative or find evidence in absence. We have the same problem with proving the effectiveness of GFCIs, AFCIs, and TR receptacles.

    Take for instance the fact that the CPSC has not reported a single injury or death as a result of a lightning strike to an indoor swimming facility. Is that true because it is safe to swim indoors during a storm or is because people get out of indoor pools during storms so injury and death is not likely to occur. If we were to change that policy and say swimming at indoor pools is safe, would the occurrence of injury and death start to rise? Why take that chance?

    Sometimes, safety rules and safety equipment need to be seen as an insurance policy. None of us want to get sick, in a car accident, or electrocuted. So, we have insurance polices to protect against those "what-ifs" in life. We all agree that rules should not be placed in the code based on what-ifs unless there is compelling evidence the absence of at that rule has led to loss of life or property. Many of our current code rules are based on the premise that something bad is likely to occur in the future but not necessarily guaranteed to occur.

    The same holds true for lightning safety. I feel this quote from the NLSI white paper sums it up nicely:

    "There is a built-in conflict between indoor pool activities and lightning safety. Both recreational swimming and competitive swimming events are based upon three icons of *Entertainment*, Health, and Pleasure. Lightning safety is founded on stopping all those forms of enjoyment. A Risk Management/Safety Professional will err on the side of caution every time and will be found harmless from allegations or claims of negligence. Such a conservative approach will find many objectors. Safety, however, is the prevailing directive."

    Bryan P Holland  October 30 2015, 9:51 am EDT
    Reply to this comment

  • This legend led my family to cancel membership at an aquatics center, traveling to it and finding out pool was closed because of pending storms. Living in the Midwesr, storms are often in the summer months.

    Mike. Kasel  October 30 2015, 9:27 am EDT
    Reply to this comment

  • " Indoor pool closures during electrical storms is a violation of the NEC section 250.4 (A)(1) according to Vicki Weiss, Ph.D. "

    Seriously ? Where did Vicki get that information ?

    Brad Darnell  October 30 2015, 8:11 am EDT
    Reply to this comment

  • It may just be a matter of common sense to get out of the pool. I personally don't feel safe taking a bath or shower when there is massive lighting going on outside. If it can explode all the TV's, Computers, and everything else in the house, we know it will look for us too!

    Drew Howard  October 30 2015, 8:02 am EDT
    Reply to this comment

  • i don't know where most of these 'theories" come from. if this was such a danger, we all would have been killed as children.

    Leon Diehl  October 30 2015, 7:32 am EDT
    Reply to this comment

  • Two conspiracy theory oriented newsletters in a row, first the noisy transformer, now this.

    What is up? Stayed up late watching old X Files episodes?

    djames  October 30 2015, 1:21 am EDT
    Reply to this comment
  • Reply from: Mike Holt   October 30 2015, 8:10 am EDT
    Yea, years ago I also knew everything...
    Reply to Mike Holt

    Reply from: John Kaldon   October 31 2015, 11:50 am EDT
    Do you have any information on lightning fatalities while taking a bath during a storm? We do not use equipotential grounding/bonding on indoor bathtubs but we do require grounding/bonding of metal water pipes. Why isn't anyone discussing "LIGHTNING PROTECTION" for the building using the lightning standard rather than discussing the NEC requirements?
    Reply to John Kaldon


  • All pool lighting should be replaced with low voltage LED lighting. Line voltage lighting is passe, and dangerous.

    Michael E Olson  October 29 2015, 10:48 pm EDT
    Reply to this comment

  • I think that lightning may not strike if the indoor pool is situated inside the concrete building. There could be a possibility if it is built inside a house built with wooden or any other insulation material( without adequate shielding shielding and grounding).As most of you know lightning is a flow of current between the charged clouds and the earth. (more details about lightning could be provided if further interested).achuthan@presevi.in is the mail ID.

    Achuthan  October 29 2015, 9:57 pm EDT
    Reply to this comment


Get notified when new comments are posted here
* Your Email:
 
        
 
Add Your Comments to this Newsletter
* Your Name:
   Your name will appear under your comments.

* Your Email:
   Your email address is not displayed.
* Comments:

Email Notification Options:
Notify me when a reply is posted to this comment
Notify me whenever a comment is posted to this newsletter