Keeping up with the requirements of the Code should be the goal of everyone involved in electrical safety. The following is what I feel is an important rule in the 2023 NEC®, complete with graphics and a video. I encourage you to use it as a training resource for your organization, and share it with your colleagues.

EGC for Receptacles and Fixed Equipment in Patient Care Spaces [517.13]
This content is extracted from Mike Holt's Understanding the 2023 National Electrical Code Video Program.

Click here or on the thumbnail to view or download the PDF of this rule. (4 pages, 1,624 KB)


Click on the image above to watch the video

During a medical procedure a patient may have a limited ability to react to an electric shock or may be completely unconscious. This risk is addressed in section 517.13 of the NEC which lays out the EGC requirements for patient care spaces in health care facilities. To ensure that the patient is protected, the branch-circuit wiring method must consist of a two-part effective ground-fault current path that is unique to patient care spaces.

The effective ground-fault current path for patient care spaces must have a metal raceway or metal cable armor that that qualifies as an equipment grounding conductor per 250.118. Additionally, there must be an insulated copper equipment grounding conductor of the wire type. Read the attached PDF then join Mike and the team on the video as they discuss the requirements of 517.13 in the NEC.

We'd love to hear from you about this series, and the ways you're using it. Send us your comments and feedback by clicking on "Post a Comment" below. Look out for the next part in this series a month from now, and please share with your colleagues.

Stay Connected:
instagram
facebook
linkedin
twitter
Comments
No comments to display
Add Your Comments to this Newsletter

Your name will appear under your comments.

Your email address is not displayed.

Email Notification Options: