Why would I use aluminum wire anyway?

The year 2020 provided me with the unique opportunity and the time to produce a series of videos on topics that you told me were of interest to you. I recorded them from my house, and livestreamed them over the course of several months. There were a lot of you that might not have been able to tune in, and others who did, but would enjoy the chance to see them again. We'll be sending them out monthly in a newsletter series. Enjoy and feel free to share!

Is aluminum wire really that bad? Is antioxidant required on aluminum conductor terminations? Why does aluminum have such a bad reputation, and why would I use it anyway?

Let's start by looking back at the history of aluminum building wire installation and terminations. Wire manufactured before 1972 aluminum wire was an alloy called AA-1350 intended for use in electrical utility applications. This conductor was 99.5% pure aluminum. When the surface of AA-1350 was exposed to oxygen, the aluminum and the oxygen would chemically bond to create aluminum oxide, causing terminations to oxidize and fail unless an antioxidant was used at all terminations. Failed connections and fires were the typical result of untreated terminations.

Today's aluminum wiring material is AA-8000 series aluminum alloy, with zinc titanium, manganese, and silicone added to the aluminum. This alloy has increased strength and resistance to corrosion and has been required in the NEC since 1981[310.3(B)]. Unlike AA-1350, neither wire brushing nor antioxidants are required for AA-8000 aluminum alloy conductor terminations. Underwriter Laboratories have tested AA-8000 terminations according to UL 486A-486B without brushing or oxide inhibitors and confirmed they meet or exceed the required standard. It is important to note that all electrical connections must be torqued per manufacturers instructions [110.14(D)] and terminals for aluminum conductors must be identified either 'AL' or 'CU-AL'.

Join Mike on this video as he answers questions and dispels the myths surrounding the use of aluminum conductors in today's modern installations.

Click here or on the image to watch the video [8min:45sec].

Comments
  • I am running into a problem with a local utility. The local utility is installing an underground submerged vault for a new building we are designing. We want to use Aluminum service conductors to save costs since due to building restrictions we are not able to locate the Main Electrical room adjacent to the exterior wall where the vault will be located and service conductor lengths will be +/- 150 feet. The local Utility is indicating that we can only use Copper Conductors coming into the Utility vault. The only explanation they are giving is that they have had an issue with Aluminum conductors, they indicate that on a previous project they had issues with galvanic corrosion as well as issues with insulation failure. We planned on using type XHHW-2 type conductors. Have you heard of these issues anywhere else with utility companies making this requirement? Also if i have copper conductors with type XHHW-2 insulation would i have the same issue of insulation failure since it is the same insulation type?

    Warren Waldrop  August 26 2021, 3:20 pm EDT
    Reply to this comment

  • Can AL, AL-Cu terminals be used for pure copper? If, why are not all terminals AL or AL-Cu

    Bob  August 25 2021, 11:57 pm EDT
    Reply to this comment
  • Reply from: Warren Waldrop   September 1 2021, 2:09 pm EDT
    Bob, I am assuming that Georgia Power made the terminations using AL-CU terminals, since the collector bus is copper and the service conductors were aluminum. But since the Utility makes all the terminations in their vault, I am not certain exactly what they use. But with this in mind, if aluminum conductors are properly terminated per the manufacturers recommendations, why would the Aluminum XHHW-2 insulation fail or fall off in the underground vault environment and the Copper XHHW-2 insulation does not fail. It seems that the insulations for both types of conductors are the same and would react the exact same way. Just curious if you have heard of this issue in other areas around the country and if there is something that can be done so that the aluminum conductors insulation does not fail.
    Reply to Warren Waldrop



Get notified when new comments are posted here